Tubes...leaking

This forum is dedicated to the Live Steam Hobbyist Community.

Moderators: cbrew, Harold_V

User avatar
NP317
Posts: 4581
Joined: Tue Jun 24, 2014 2:57 pm
Location: Northern Oregon, USA

Re: Tubes...leaking

Post by NP317 »

Emfinger wrote: Sat Jan 16, 2021 11:20 am [snip]
The steam dome only has a few 1/4" holes into the boiler.
Tom
Time for that endoscope.
I purchased an inexpensive one on Amazon that works with my smart phone via wi-fi interface.
Find the smallest diameter camera end available: usually 5mm or less. Very useful.
RussN
User avatar
Bill Shields
Posts: 10525
Joined: Fri Dec 21, 2007 4:57 am
Location: 39.367, -75.765
Contact:

Re: Tubes...leaking

Post by Bill Shields »

Perhaps you could 'scope' down one of the boiler fittings - say the safety valve..which may well have a larger diameter hole.

if / when you decide to retube the boiler, suggest you get that 'opening' made = ID of the steam dome ring so that you can get in and 'look about' occasionally.

Southern CA has a large number of steamers and clubs, and (used to have) multiple representatives of the boiler building / repair trade. Since I make my own, i have not really looked specifically in that area this millennium (or earlier).

However, once you get the boiler off and on a pallet...you may well find that the most competitive / competent repair / replacement agency is 1/2 a country away (say middle America)...at which point it is just shipping charges...
Too many things going on to bother listing them.
Emfinger
Posts: 229
Joined: Tue Oct 01, 2019 3:30 pm
Location: Yucca Valley, CA

Re: Tubes...leaking

Post by Emfinger »

You can blow up the picture and see that the tubes look welded, but not to the sheet. So are the rolled of welded???
Thank you
Tom
Attachments
IMG_0003.JPG
User avatar
milwiron
Posts: 156
Joined: Sun Jun 07, 2020 1:52 pm
Location: Flanagan, IL.

Re: Tubes...leaking

Post by milwiron »

Welded but some of the beads don't penetrate the sheet. That's the way it appears to me.
Denny
"Measure twice, curse once."
Emfinger
Posts: 229
Joined: Tue Oct 01, 2019 3:30 pm
Location: Yucca Valley, CA

Re: Tubes...leaking

Post by Emfinger »

None of them have penetrated the sheet...not welded to the sheet......what the sheet? The leak is on the inside, just behind the "weld" or rolled lip ? I'll retest with pressure but the rust in the other tubes is from me blowing out the firebox and blowing water into several tubes.
I refilled the boiler and the water poured out...from that one tube. By morning the water was all gone (down to the tube)

Anyone know of a 40 year old procedure that involves welding the lip of the tube..but not to the sheet?

Thanks
Tom
User avatar
Bill Shields
Posts: 10525
Joined: Fri Dec 21, 2007 4:57 am
Location: 39.367, -75.765
Contact:

Re: Tubes...leaking

Post by Bill Shields »

So...what would one weld the tube TO? Itself?

Tubes might be proceened (spelling)...but then I have only seen that done on a model boiler once or twice in 50 years. It is a process where the end of the tibe is rolled over after the tube is rolled into the sheet.

However based on what I see here and in the previous picture. I would just offer that it is just a crappy no penetration weld job

Water pouring out is a confirmation that tubes need to be replaced
Too many things going on to bother listing them.
FKreider
Posts: 339
Joined: Fri Feb 02, 2018 8:44 pm
Location: Massachusetts

Re: Tubes...leaking

Post by FKreider »

What I think we might be seeing here is the tubes were originally welded to the tubesheet however as suggested above the weld did not properly penetrate. Over the years as the boiler was heated and cooled and the metal contracted and expanded the tubes/welds have basically pulled away from the tubesheet allowing the leaks that you are seeing now.
-Frank K.
User avatar
Bill Shields
Posts: 10525
Joined: Fri Dec 21, 2007 4:57 am
Location: 39.367, -75.765
Contact:

Re: Tubes...leaking

Post by Bill Shields »

Agreed...

A polite and astute way of describing a crappy weld job

Stay bolt welds do not look terribly spiffy either...looks like something I would do :shock:
Too many things going on to bother listing them.
User avatar
LVRR2095
Posts: 1690
Joined: Sun Mar 04, 2007 6:50 pm
Location: Maine, USA

Re: Tubes...leaking

Post by LVRR2095 »

Bill Shields wrote: Sun Jan 17, 2021 4:24 pm So...what would one weld the tube TO? Itself?

Tubes might be proceened (spelling)..
Bill, I think you may be referring to the Prosser method of tube installation where the tube is expanded behind the tube sheet, then rolled and beaded.

Keith
User avatar
Bill Shields
Posts: 10525
Joined: Fri Dec 21, 2007 4:57 am
Location: 39.367, -75.765
Contact:

Re: Tubes...leaking

Post by Bill Shields »

That is it...thanks..but I doubt it is the case here
Too many things going on to bother listing them.
Marty_Knox
Posts: 1727
Joined: Thu Jan 09, 2003 6:50 pm
Location: Michigan, USA

Re: Tubes...leaking

Post by Marty_Knox »

Proper installation of steel tubes consists of rolling the tubes in the sheet with about 1/8" projecting,
seal welding the tubes to the sheet, and then re-rolling.
rkcarguy
Posts: 1730
Joined: Tue Aug 22, 2017 10:33 am
Location: Wa State

Re: Tubes...leaking

Post by rkcarguy »

From what I can see in the pictures, the welds look like they lack penetration somewhat, but I would guess that the tube has cracked or corroded right behind the weld in the "heat affected zone". Unfortunately, time to tear it down and re-tube the boiler. If it's 40 years old, it's probably time.