Rotary or static converter?
Re: Rotary or static converter?
I used a static converter on a Jet mill with a step head 2 speed motor. It worked fine because there wasn't a lot of mass to start moving.
On another note, I had a 14" Jet lathe that was a gear head with a 2 hp motor in it. The same static converter would only run the lathe at lathe below 500 RPM. I actually blew out the capacitor in the static converter after a few attempts to run at a higher RPM. It required a rotary phase to work.
On my present lathe a 16" Pratt & Whitney I am running what I think is 10 HP rotary phase converter. Its label is missing. Its a real old school converter from back in the day when 3 phase wasn't available. My lathe has a 7 1/2Hp motor under it. Under a heavy cut it wasn't the converter that had problems, but the 40 AMP breaker tripped. Still haven't upgraded the breaker to a 50AMP yet. The welder requires a 50 AMP but works fine so far with the 40 AMP breaker.
Richard W.
Richard W.
Richard,
Keep in mind, the breaker's purpose is to protect the wiring to the receptacle. If you replace the breaker and the wire isn't upgraded, you may find that the wire runs hot when you're drawing a heavy load. Switching to a larger breaker may not be a good idea.
I have kept that in mind. I am running 8 Gage wire. I run the lathe and welder from the same cord, since being one person there is no danger of running both machines at once.Harold_V wrote: ↑Fri Mar 19, 2021 3:01 pm Richard,
Richard W.
I have a lincoln Idealarc Tig 300 That draws 100 amps at full power. I have 4 gage wire to the outlet but have only a 60 amp breaker in the box as that was all I had. I have never tripped the breaker but then I have never used it at full power . Maybe someday when I feel rich I will upgrade that breaker.
Jack
Jack
That is my situation. I have a Miller Thunderbolt stick welder. I use 1/8" 7018 rod mostly. So I never crank the welder up to full AMP draw.JackF wrote: ↑Sat Mar 20, 2021 11:39 am I have a lincoln Idealarc Tig 300 That draws 100 amps at full power. I have 4 gage wire to the outlet but have only a 60 amp breaker in the box as that was all I had. I have never tripped the breaker but then I have never used it at full power . Maybe someday when I feel rich I will upgrade that breaker.
Jack
Richard W.
8 AWG is too small for the current you are pulling.
Depends on the insulation. If it's in a raceway and THHN (or equivalent), or in a cable, it's perfectly safe. Rated @ 50 amps. Even higher with open wires. That's assuming it's copper, not aluminum wire. If the wire is either aluminum or type TW or UF, yeah, it's not suited (rated @ 40 amps).BigDumbDinosaur wrote: ↑Sun Mar 21, 2021 2:05 am8 AWG is too small for the current you are pulling.
Except it's powering a motor, which is an inductive load, not resistive. Unless the motor's power factor is unity (which is unattainable without use of power factor-correcting capacitors), KVA will be greater than watts, resulting in higher than apparent current flow.Harold_V wrote: ↑Sun Mar 21, 2021 4:12 amDepends on the insulation. If it's in a raceway and THHN (or equivalent), or in a cable, it's perfectly safe. Rated @ 50 amps. Even higher with open wires. That's assuming it's copper, not aluminum wire. If the wire is either aluminum or type TW or UF, yeah, it's not suited (rated @ 40 amps).BigDumbDinosaur wrote: ↑Sun Mar 21, 2021 2:05 am8 AWG is too small for the current you are pulling.
Its an 8 gauge SO cord all copper. It was made for the welder.Harold_V wrote: ↑Sun Mar 21, 2021 4:12 amDepends on the insulation. If it's in a raceway and THHN (or equivalent), or in a cable, it's perfectly safe. Rated @ 50 amps. Even higher with open wires. That's assuming it's copper, not aluminum wire. If the wire is either aluminum or type TW or UF, yeah, it's not suited (rated @ 40 amps).BigDumbDinosaur wrote: ↑Sun Mar 21, 2021 2:05 am8 AWG is too small for the current you are pulling.
Richard W.
Generally SO and SJ cords are copper...never seen any that is not.. .and I have used a lot of it in the last 50 years. => but there is a lot of stuff out there that I have never seen.
Just look at it...if it looks like copper when you cut the insulation off..then it is copper.
This entire matter is a little tricky. The motor is reported to be 7½ horse, but the rotary is assumed to be 10 horse. Running from single phase 240 volts, the recommended breaker would be 90 amps (for a 10 horse motor), while it would be 80 amps for a 7½ horse motor. Wire size for the 90 amp would be #6, while wire size for the 80 amp would be #8. This according to the Motor Data Calculator published by Square D.
That is not to say that the setup won't work with a 50 amp breaker. It will, and it will be perfectly safe. If there are any issues, it will be with tripping the breaker, which would be likely to happen if the motor was cycled on and off regularly, or if it was subjected to a full load continually. Neither scenario is likely to happen. Go for it!
I agree completely. These current ratings for conductors and breakers are for an assumed continuous full load. I suspect that most home shops aren't running a continuous 80 or 90 Amp load.Harold_V wrote: ↑Wed Mar 24, 2021 1:43 am This entire matter is a little tricky. The motor is reported to be 7½ horse, but the rotary is assumed to be 10 horse. Running from single phase 240 volts, the recommended breaker would be 90 amps (for a 10 horse motor), while it would be 80 amps for a 7½ horse motor. Wire size for the 90 amp would be #6, while wire size for the 80 amp would be #8. This according to the Motor Data Calculator published by Square D.
I have a single 240V, 50A single phase receptacle in my small shop that I share between my welders and my 10HP RPC. The receptacle is fed from a 50A breaker via #6 wire and I have never experienced a single issue in the 10 years it's been in service.
Ted